MCC Breaker Handle Height

Status
Not open for further replies.
I understand that 240.24 requires the handle for the overcurrent device to be 6'7", but does that apply to a MCC?

MCC has a main breaker that is below 6'7". Each load fed from the MCC has a disconnect at the load.


Thanks,
Jasen
 

lakee911

Senior Member
Location
Columbus, OH
I understand that 240.24 requires the handle for the overcurrent device to be 6'7", but does that apply to a MCC?
Why wouldn't it apply to an MCC...unless the device in question wasn't an over current device.

Also, I think thats the max. height mean that it has to be less than that. I think you might also need to take into consideration that the handle would be up when on (and higher) and the equipment may be on a housekeeping pad, or curb, again raising it higher.

MCC has a main breaker that is below 6'7".
Sounds like you're good to go then.
 
I was wondering, since it had a main that shut down all the breakers, did the individual breakers need to meet the 6'7"?
 

jumper

Senior Member
It cant be higher than 6' 7", isnt that what you mean. And yes it would need to meet those requirements.

Yep . Here is a pix.

1100118905_2.jpg
 