MCC feeding second MCC in another building.

Status
Not open for further replies.

rrc14

Member
Location
Anchorage, AK
Occupation
Engineer
I have a MCC that will feeding a second MCC in another building, does the NEC require a ground rod for the second MCC? We will be installing 3 phase conductors and a ground from the first MCC to the second MCC.

Thanks,
 
NEC 250.32 requires a grounding electrode system at the 2nd building
consisting of the electrodes listed in 250.52
 
Last edited:
You might also check the requirements of 225.30, 225.32 in reraged to the required disconnecting means.
 
I have a MCC that will feeding a second MCC in another building, does the NEC require a ground rod for the second MCC? We will be installing 3 phase conductors and a ground from the first MCC to the second MCC.

Thanks,

The MCC does not require a GES, but the second structure does.

Does the second building already have power?
 