Besoeker you were right when you said that a 22kW motor should have been selected. I went to one of the seniors and he said that in actual a 22kW motor was used with a 30KW VFD and not an 18.5KW motor.(He had no idea why Mr. Rajesh told me that 18.5KW motor was used) After that I did some calculations again.
I don't know why a 30kW VSD would be selected without some justification for doing so. The 22kW VSDs in production with us have an output current rating of 46A. For a 22kW fan/pump motor load that ought to be adequate. Unless the motor has an uncharacteristically low efficiency or power factor. But we seem to have no information to that effect.
30KW VFD has an input current of 55A, now if i multiply it by 150% it turns out to be 82.5A. Now does it make sense to use a 100A MCCB
Again, I don't know where the 150% comes from. You mentioned IEE or IEC standards. As far as I'm aware, there is no such requirement stipulated.
On that basis I'd still go for a 63A input MCCB or fuse switch.
Now as for wire size I have the folliwng info and my calculations are as follows,
Type of conductor = Copper
Installation Method =
Distance = Not more then 70ft
Ambient Temperature = 30C
Full Load Current = Ia = 55A
MCCB = 100A
Current Rating for Cable = Iz = 1.25*100 = 125A
Again, the 1.25 factor and the 150% are not factors that I know of that need to be applied.
From the table I have its says that a 25mm2 has an amperage rating of 124A and 35mm2 has an amperage rating of 154A. So i use a 35mm2 4 core cable. Is this right??
Rating the conductors at nearly three times the steady state drive input current is not something I would do or have ever needed to.
I don't know what table you are using but I use BS7671 which is the IEE standard for wiring regulations.
I assume that, given the application, you would be using Multicore armoured pvc insulated so table 4D4A* would apply.
From that 10mm
2 gets you 62A in a four core configuration for usual installation practice. That should more than suffice for an input current of 55A in a 30C ambient.
*This from an older version of BS7671 - my more up-to-date version has gone walkabout, last known whereabouts in my office at work. If I was an angry person I'd kneecap the culprit. IRA style.
But I'm a benevolent old chap. I'll just behead him......keeps the suffering brief you see......