I deviated an residential dwelling electrical plan for not providing GFCI protection on a receptacle located in a master bedroom, which was within 6 ft. of the edge of a bathtub (located in the master bathroom). It did not show a door.
He stated they would install a bathroom door and that would be hung so that it swing out (into the bedroom). Therefore the measurement should be taken starting from the receptacle and measuring around the open door (door will open 180? laying flat against the bedroom wall, covering over the receptacle).
This would decrease the 6 ft. measurement by 2 ft. (one foot over to the edge, and one foot back), allowing only a remaining four foot cord for measurement. Therefore the receptacle would no longer be within six-foot of the edge of the bathtub. I agreed and accepted the receptacle without GFCI protection.
However as this is a new code requirement, I thought I might ask for other opinions. As far as I know, it's never been discussed (that I know of) but the measurement is taken with the door in consideration, is it not? Or should it be straight-lined, ignoring the door?
--
2014 NEC: 210.8(A)... "(9) Bathtubs or shower stalls -- where receptacles are installed within 1.8 m (6 ft) of the outside edge of the bathtub or shower stall."
He stated they would install a bathroom door and that would be hung so that it swing out (into the bedroom). Therefore the measurement should be taken starting from the receptacle and measuring around the open door (door will open 180? laying flat against the bedroom wall, covering over the receptacle).
This would decrease the 6 ft. measurement by 2 ft. (one foot over to the edge, and one foot back), allowing only a remaining four foot cord for measurement. Therefore the receptacle would no longer be within six-foot of the edge of the bathtub. I agreed and accepted the receptacle without GFCI protection.
However as this is a new code requirement, I thought I might ask for other opinions. As far as I know, it's never been discussed (that I know of) but the measurement is taken with the door in consideration, is it not? Or should it be straight-lined, ignoring the door?
--
2014 NEC: 210.8(A)... "(9) Bathtubs or shower stalls -- where receptacles are installed within 1.8 m (6 ft) of the outside edge of the bathtub or shower stall."