Look at # 3 below from 210.52. This would not allow this installation.
210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. The receptacles required by this section shall be in addition to any receptacle that is:
(1) Part of a luminaire or appliance, or
(2) Controlled by a wall switch in accordance with 210.70(A)(1), Exception No. 1, or
(3) Located within cabinets or cupboards, or
(4) Located more than 1.7 m (5? ft) above the floor
Edit to add: This would not allow this installation to be the lone receptacle required.
If it is inside of the cabinet, it is still permitted. It would not meet the requirement for the minimum set forth for bathrooms, and an additional receptacle would be required.