brian john
- Kilmarnock, Va
- Retired after 52 years in the trade.
When any testing raises questions, Stand back and think what am I missing, isolate and re-test.
I always start with 50V and when I got the low reading, I stopped.brian john said:When any testing raises questions, Stand back and think what am I missing, isolate and re-test.
gar:gar said:090704-1853 EST
wptski:
You were testing with a source voltage of 50 V from your earlier post. This is well below the the normal applied voltage to the breaker circuitry (120 V RMS, +/-170 peak). If your megger source resistance was high enough you might not damage the GFCI with a higher voltage.
I see. The reason you start with a low voltage is to double-check for missed connected loads. When you get a bad reading right off the bat like that, you've got something still connected. In resi, it's stuff like GFCI's, dimmers, lamps, furnaces, chime transformers, attic fans, etc.wptski said:I always start with 50V and when I got the low reading, I stopped.
I forgot to mention that I always start by using the resistance function of the Fluke 1507 but a max reading will show as >22.00K and then proceed to insulation at 50V. A reading with a DMM showed 9.5M with the GFCI on the circuit.mdshunk said:I see. The reason you start with a low voltage is to double-check for missed connected loads. When you get a bad reading right off the bat like that, you've got something still connected. In resi, it's stuff like GFCI's, dimmers, lamps, furnaces, chime transformers, attic fans, etc.
The Shock-Buster isn't a typical GFCI. I also failed to mention that I piggybacked the it into the Leviton and it didn't function as before.gar said:080704-2218 EST
wptski:
If you noticed the National sample circuit had an MOV and a bridge rectifier at the input across line to neutral. A typical DMM will only use a low source voltage for measuring resistance. Hardly enough to forward bias a diode or two and also there is probably a substantial internal current limiting reasistance in the meter.
At the 50 V level you are going to activate more of the electronics. I have never tried proding a GFCI to see how it responds, and so I have no idea about the reset.
wptski said:The Shock-Buster isn't a typical GFCI. I also failed to mention that I piggybacked the it into the Leviton and it didn't function as before.
There's a new low ohm function in the Fluke 289 for testing motors that uses 20V. I wonder how that would work?
Nope, the 1507 is >4.0V <8.0V.76nemo said:That's the same low-ohm function that is on the 1507, is it not???