Also I just received an email from someone who was on site when the events happened. Note that at this facility, most of the lights, workstations, and things you would notice as being off, are on the generator and ATS. The circuit that burned up and made the smoke feeds that rigged transformer which feeds three AC compressors. Seems clear that the utility phase loss happened first:
What I dont quite understand though is why the power appeared to be completely off for nearly 10 minutes. I dont know how the ATS handles a phase loss, but I would assume it would start the generator and transfer as soon as the generator source was accepted which should be about 10 seconds.
I arrived on Sunday at 12:00pm, some of the lights downstairs were
either off or flickering, but to the best of my knowledge everything
else seemed fine.
At roughly 3:00PM the power went off completely; ~3:10PM the power came
back on at a reduced capacity, I presume the generators were running at
this time.
~4:30 - 5:00PM the fire alarm went off, and the smell of burning rubber
was becoming more and more evident.
What I dont quite understand though is why the power appeared to be completely off for nearly 10 minutes. I dont know how the ATS handles a phase loss, but I would assume it would start the generator and transfer as soon as the generator source was accepted which should be about 10 seconds.