I do have a customer who heed to set up a small repair shop from the metal container.
He wants to install a compressor and few 110 V general outlets and some lights.
The container is feed from adjacent building with some branch circuits ( no panel inside the container).
My question: Does the container needs to be bounded to the electrical circuits?
does the container need to be grounded to his own grounding rod?
 

iwire

Moderator
Staff member
Location
Massachusetts
First problem, multiple branch circuits to a separate building or structure are a violation. 225.30


You need to put a panel in the container and run a feeder to the panel.

Then you will have to install a grounding electrode or two. 250.32(A)

You will also have to have a service rated disconnecting means. 225.36
 

iwire

Moderator
Staff member
Location
Massachusetts
what if the panel have less than 6 circuits does it have to be service disconnect with the ground rod?

Yes, but if you just used a main breaker load center you would be all set.

You really need to read 225.30 - 225.39 and 250.32, those few sections spell it all out.
 