Metallic conduit body between PVC runs.

Status
Not open for further replies.

Carultch

Senior Member
Location
Massachusetts
Guys installed metallic conduit bodies between runs of PVC. Any solution to bond these other than drill and nut and bolt a lug to them? No clue why they didnt install EMT.
If you drill the body to install a lug, you end up with an issue of voiding the product listing. Perhaps a bonding U-bolt or bonding strap around the circular hubs might work, in which case you'd need a #6 bonding jumper running to a point where you can connect it to the EGC system.
 