Re: meter banks
yep.
yep.
Wayne it may come down to making a code that works for all situations. we have done some very large buildings, 45 acres (almost 2 million sq ft.) large in one case.Originally posted by hurk27:
I truly believe that when a single structure (like a church) under one management each building should only have one set of not more than six disconnects. This is my own belief.
I understand that, my point was really that the code already allows more than 6 disconnects to one occupancy.Originally posted by hurk27:
Bob a building that large is already covered under 230.2(B)(2)
No exception is needed in 230.40
Two or more service's means two or more service drops and/or latterals!A single building or other structure sufficiently large to make two or more services necessary
Unless you can meet one of the five exceptions.Each service drop or lateral shall supply only one set of service-entrance conductors.
which to me would inicate that the disconects would have to be grouped at one location.supply separate loads from one service drop or lateral,