raul trevino
Member
my question: can you have the service & load wires cross from inside the meter box.
If what you mean is the service conductors connected to the line side of the meter base and the other set of conductors also service conductors, connected to the load side of the meter base, there would be no problem with these conductors crossing one another.
If what you mean is the service conductors connected to the line side of the meter base and the other set of conductors also service conductors, connected to the load side of the meter base, there would be no problem with these conductors crossing one another.