Creating an effective path to ground
Creating an effective path to ground
Keep in mind that your ultimate goal is to create an effective low resistance path to ground for the metallic parts of your service conductor raceway. This is not intended to be a part of your grounding electrode but instead provide adequate arc protection for the raceway. If non ferrous is required in your application, ie Florida outside, the replace the raceway with non ferrous. If it's not required or perferred then bond the load side of all your metallic service conductors, always. It doesn't take much and it shows that you care. Have a great day
Creating an effective path to ground
Here PVC is the "preferred" method if there are no hubs involved as metallic conduit would require a bonding bushing.
The Code pretty much ignores the "parallel path" created by the metal nipple in this situation.
Keep in mind that your ultimate goal is to create an effective low resistance path to ground for the metallic parts of your service conductor raceway. This is not intended to be a part of your grounding electrode but instead provide adequate arc protection for the raceway. If non ferrous is required in your application, ie Florida outside, the replace the raceway with non ferrous. If it's not required or perferred then bond the load side of all your metallic service conductors, always. It doesn't take much and it shows that you care. Have a great day