Meyer's Hub
ryan_618
For the purposes of 250.92(B)(2) and (B)(4), would you call a Meyer's hub a "threaded boss on an enclosure"? Would you say that they utilize "standard locknuts"? Would you say you need a bond bushing on a Meyer's hub if it is on the line side of a service?
1. No
2. Yes, although the contact surface is larger
3. Yes
Yes. I think the term "threaded boss" is to be clear that it is NOT an emt connector or an FA (for pvc). (In foundry terms: "A projection of circular cross-section on a casting. Usually intended for drilling and tapping for attaching parts.)
As to the bond bushing... No. The four bolts through the enclosure do that.
THe critter you picture is also what I call a Myers Hub. To me, it meets the requirements of 250.92 without requiring a bonding locknut or bushing, and I do not consider any part of it a "standard locknut"
I also call Rob's picture a Myers Hub but the ones that I normally use are a little different. They are Red Dot's HTZ series hubs.
For this style there is not a way to put a bonding bushing on them.
never heard of "JB WELD" ? :D
inspector wants a bushing:smile:
A Meyers Hub has a rubber O-Ring. I say a bonding bushing is required.
Obviously, there is more than one manufacturer, but on, the ones I have used, the O ring is recessed enough that the "teeth" of the hub still bite into the enclosure. To me, and perhaps only me, that is sufficient.
same here.
i don't think a bonding bushing is required.
that's what the teeth are for, right?
I just looked at one on my truck and it does seem to have 5 threads
in contact as well. Still the O-Ring isn't recessed enough IMO because
if it were it wouldn't be rain tight.
the o-ring compresses when you tighten the hub, giving you full contact of the metal surface with the enclosure, and a water seal.
While I agree that a myers hub is not a thread boss and some form of bonding would be required if you used it for a service raceway, it is my opinion that a myers hub provides a better bonding path than a meter hub where the bonding path is really just the screw threads.
IMO, I would agree that the lock nut that comes with a "standard male 'Myers' hub" fitting is a trade standard lock nut. However, in the past I have used female Myers hubs that do not include a locknut as part of its standard assembly.
Some male Myers hubs come with a bonding style locknut.