I dont think you can legally put a bond bushing on most meyers hubs.

you would have to remove the 'lock nut' to gain enough threads.

we all know you cannot use a bushing as a lock nut.

leave well enough alone

meyers hubs do include something more substantial than 'a standard locknut', and as so, meet the requirements for bonding at the service
 
...
we all know you cannot use a bushing as a lock nut. ...
The code only says you can't use a bushing made wholly of insulating material can't be used in place of a locknut. 300.4(G) A grounding bushing is a metallic bushing and like any metallic bushing can be used in place of the interior locknut. Having said that you can't really use a grounding bushing in place of the locknut on a hub. The hub locknut has to be made up tight to make the seal against the hub's O ring. It is unlikely that the bushing would be able to do that.
 
The code only says you can't use a bushing made wholly of insulating material can't be used in place of a locknut. 300.4(G) A grounding bushing is a metallic bushing and like any metallic bushing can be used in place of the interior locknut. Having said that you can't really use a grounding bushing in place of the locknut on a hub. The hub locknut has to be made up tight to make the seal against the hub's O ring. It is unlikely that the bushing would be able to do that.

Plus, using a bonding bushing as a fitting locknut is probably not the use it was intended or listed for. ;)
 
Are you saying we can't use it in place of a standard locknut on conduit, or just that we can't use it on a hub?

If it is a standard bonding bushing, it should not solely be used as a fitting locknut because it is probably not listed for that use. Bonding bushings have different specification requirements (UL467) than fitting locknuts (UL514B) and would not be tested for use as a locknut function.

As for using it on a myers-style hub with the wider locknut, there will not be enough threads left on the hub body to adequately secure an additional bonding bushing. 344.46 intends for a bushing to protect the conductors but not support the conduit. In 300.4(F), it specifically prohibits NM bushings from being used to secure a raceway or fitting, but does not mention anything about metallic bushings being used for such purpose.

This being said, there are a few bonding bushings out there that can be used to support Rigid conduit like a locknut and provide a bonding point (i.e. T&B "BlackJack). However, I do not believe that bushing is listed for use with any fitting. I looked at the listing and there is no mention of being used with fittings in place of a locknut - like a hub or standard connector.

There are other manufacturers that make insulated, bonded, hubs (i.e. T&B).
 