kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
Potentially has a violation of 334.15(C) in that drawing.
Potentially has a violation of 334.15(C) in that drawing.
This rule not necessary IMO. Is a step in the direction of "lets GFCI protect everything" and has no good basis. Yes I believe there was an electrocution from an AC unit that had a fault and missing or compromised EGC used as justification. Assuring there is sufficient EGC would have also saved that person.
View attachment 2555317This was able help me explain to people better than I could verbally. Maybe help someone else.
Just to prevent debris from falling in the pipe. Duct seal does the job.(4) Raceway is “sealed”?
View attachment 2555317This was able help me explain to people better than I could verbally. Maybe help someone else.
Is it permissible to have the GEC to not be continuous on a communication system? What if you had a fitting listed for termination of more than one conductor?. I’m just curious.
Typically used/required intersystem bonding devices are exactly what you described.Is it permissible to have the GEC to not be continuous on a communication system? What if you had a fitting listed for termination of more than one conductor?. I’m just curious.
Just use a second fitting.Is it permissible to have the GEC to not be continuous on a communication system? What if you had a fitting listed for termination of more than one conductor?. I’m just curious.
I like the can of "something" at the bottom right under the floor. Who hasn't seen that at some point? Something, something, "Extra Thick".