I’ve got an application where the customer says he’s controlling each of his field lighting pole lights with its own 480 volt 3 phase 80amp breaker. Breakers are beginning to fault. I’m looking for simplest modification to switch with disconnects or lighting contactor/ control box on poles.
any specific recommendations
 
Sounds like the CB's are failing because they're being used as switches. How many 3 pole 80 amp CB's are involved?
 