don_resqcapt19 said:I have never seen a minimum and maximum rating for the OCPD.

I've seen quite a few lately that list the min and max ocpd.
don_resqcapt19 said:I have never seen a minimum and maximum rating for the OCPD.
I would install #10 with a 45-amp breaker and a 60-amp non fused disconnect. :smile:SmithBuilt said:![]()
I've seen quite a few lately that list the min and max ocpd.
Minuteman said:I would install #10 with a 45-amp breaker and a 60-amp non fused disconnect. :smile:
LLSolutions said:I asked an AC tech and his answer was the max is the most it will ever draw on the hottest day in hell before the unit shuts itself down from internal protection. Min is the minimum it will draw usually on start up.
Not sure what you are asking. The compressor and fan motor overloads are internal parts of the motors.glene77is said:Minuteman,
Are your Overloads to be based on the FLA?
.8 * 1.25 = 10 Amps
glene77is said:Minuteman,
Are your Overloads to be based on the FLA?
.8 * 1.25 = 10 Amps