don_resqcapt19 said:
I have never seen a minimum and maximum rating for the OCPD.


AC.jpg


I've seen quite a few lately that list the min and max ocpd.
 
I asked an AC tech and his answer was the max is the most it will ever draw on the hottest day in hell before the unit shuts itself down from internal protection. Min is the minimum it will draw usually on start up.
 
LLSolutions said:
I asked an AC tech and his answer was the max is the most it will ever draw on the hottest day in hell before the unit shuts itself down from internal protection. Min is the minimum it will draw usually on start up.


You really needed to ask an AC tech this?
 
glene77is said:
Minuteman,

Are your Overloads to be based on the FLA?

.8 * 1.25 = 10 Amps
Not sure what you are asking. The compressor and fan motor overloads are internal parts of the motors.

The Minimum supply circuit amps is 27. With that given I would install #10 condutors. The Max breaker size is 45 amps, so I would install a 45 amp breaker.
 