Min size conductor and 250.122(B)

Status
Not open for further replies.

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
210.19(A)(1) says to pick larger of the two but in my case they are the same???
So now go to 240.4...

Is the #8 protected by a 50A c/b (as required by 625.41) in accordance with it's ampacity specified in 310.15 (an ampacity of 40)?

The answer is no. A conductor with an ampacity of 40 cannot be protected by a 50A c/b, so you need a larger conductor.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
So now go to 240.4...

Is the #8 protected by a 50A c/b (as required by 625.41) in accordance with it's ampacity specified in 310.15 (an ampacity of 40)?

The answer is no. A conductor with an ampacity of 40 cannot be protected by a 50A c/b, so you need a larger conductor.

But the way I see it you go to 210.20 which says to comply with 210.20(A) through 210.20(D) which then refers to 240.4. From that I do see where you are coming from
 