I am saying that you calculate the min load to the garage
Than decide if you want one branch circuit. (Min of 15 amp 14 awg, not 16 or 18 gage
Two branch circuits (min of 30 amp min of 10awg)
More than two branch circuits( 60 amp a min of 6 awg)
It's the min of the calculated load and the min of a 15, 30 or 60 amp supply conductor
The scope of article 225 is the supply conductors and the electrical equipment associated with protecting the supply conductors.
Than decide if you want one branch circuit. (Min of 15 amp 14 awg, not 16 or 18 gage
Two branch circuits (min of 30 amp min of 10awg)
More than two branch circuits( 60 amp a min of 6 awg)
It's the min of the calculated load and the min of a 15, 30 or 60 amp supply conductor
The scope of article 225 is the supply conductors and the electrical equipment associated with protecting the supply conductors.