Adamjamma
Senior Member
- Location
- Jamaica and london
If I remember correctly, though it has been over 20 years since I last did any USA Electrical, garages are only required a single 20 amp circuit, not an MWBC.Although rarely enforced here, I am of the opinion the 210.119C)(4) along with 210.70(A)(2)(2) requires a minimum of a MWBC.
Nor requirement for subpanel.
Now, if you are putting a sub panel in, even here in Jamaica, you size the feeders to your main breaker, wither it is an actual main breaker or a side feed or reverse feed breaker, that has to be locked down so it can not be pulled by accident.
I personally would use 6 gauge wire and a 50-60 amp breaker, then would have plenty of capacity for running saws, air compressors etc- and personally would run it as 240/120.. Plus would probably use a 2 inch conduit from house to it, so could pull bigger wire if needed later..
But it is always customer checkbook against job requirements.. NEC is minimum code, not required design maximums.