Maybe it would be helpful if I stepped through my methodology for sizing conductors and then someone can tell me where I messed up.
The code says to size motor circuit conductors at 125% of FLA shown in Table 430.250, so for 20HP, 460V FLA is 27. 125% of 27=33.75A. I then go to ampacity table 310.15(B)(16), look at ampacities in 75 deg. column, see that #10 is rated 35A, but notice double asterisks next to 10, so proceed to 240.4(D), which ultimately takes me to 240.4(G), which makes it permissable to provide overcurrent protection per Article 430.
Stop! You're done. You've sized the conductor correctly at #10awg.
Now lets look at overcurrent protection per Article 430.
In Article 430 I find no information which states that 240.4(D) does not apply (at least for #10s). So I apply the requirements of 240.4(D), and since the overload protection (sized at 125% of nameplate FLA) is likely to be greater than 30 and is providing the conductor overcurrent protection as allowed in 430, I bump the size to #8. So apparently everyone is saying this is not required because 240.4(G) permits you to protect per 430? Having trouble connecting those dots.
240.4(D) says that #10 conductors shall be protected at not more than 30A, unless specifically permitted in 240.4(E) or (G).
240.4(G) says that "overcurrent protection for the specific conductors shall be permitted to be provided as referenced in Table 240.4(G). Looking at Table 240.4(G), you see that "Motor and motor-control circuit conductors" are a listed "specific conductor." The Table sends you to Article 430, Parts III and IV specifically.
Art 430 Part III tells you how to protect the motor circuit conductors against overload."
Art 430 Part IV tells you how to protect the motor circuit conductors against short-circuit and ground-fault. Part IV allows an Inverse Time circuit breaker to be sized at 250% of the motor FLA, using the next standard size up. For the 20HP, 460V motor, this allows a maximum c/b size of 70A.
So the Code permits #10awg motor circuit conductors supplied from a 70A c/b with overload protection as required by Art 430 Part III.
Now if anywhere in the code it stated that 240.4(D) didn't apply to motor circuits, would make complete sense. But to just say, well because you're allowed to refer to 430, then 240.4(D) doesn't apply? Huh?
240.4(D) ITSELF says that it doesn't apply to motor circuits.
Unless SPECIFICALLY PERMITTED in 240.4(E) or (G), the overcurrent protection shall not exceed that required by (D)(1) through (D)(7).
240.4(G) SPECIFCALLY PERMITS overcurrent protection for motor circuit conductors to be other than required by (D)(1) through (D)(7).