Adamjamma
- Jamaica and london
Since it is pvc I would really like to know how the bond was made... I know how I would achieve it in the Caribbean... due to 5he building techniques... but it is against the codes there..lol...
Will do. I’ll go by and shutter-bug away. I’d like to pull the meter, but can’t.I suspect there is an unfound bond someplace and possibly more than one.
OP.
Time to get the meters out and take pictures for us.
So here are the two hot legs coming into the panel.
You can see the bare ground wire coming in from outside.
And you can see where it attaches to the grounding/neutral buss.
Also, I checked out the water meter, there is no grounding wire on the plumbing pipes.
Do you have an electric water heater or any other equipment that is in contact with the plumbing? You may not see a 6 bare directly connected to the WP.
Is there a common metallic water piping system in the neighborhood? Clamp your amp meter around the water line as it leaves the house. Do the same for any other piping system. Some current is normal on these but you should be able to see a significant change in current as you cycle 120v loads in the house.
Do you have an amp clamp meter?
Water heater is gas.
House alone in woods. No common bond in neighborhood.
Welll so much for my SEWAG!
Gas heat?
Propane tank or natural gas line?
at this point I would have to guess that there is an underground bond from the ground rod at the panel to the poco ground, or an overlooked or hidden bond to metal water pipe.
Natural gas, no bond on there either.Welll so much for my SEWAG!
Gas heat?
Is this house located in Cornwall, NY?
If so, you are required to hold a Rockland County Electrical license (or work for a licensed holder) to perform electrical work.
no disrespect intended, but from your profile, you don't seem to qualify.
Best of luck!
EGC to a furnace could possibly be carrying neutral current, though NG usually has isolating fitting somewhere near the point of emerging from underground and/or at metering equipment.Natural gas, no bond on there either.
Well, it's worked fine since 1990, maybe I could just run a single neutral to the meter. :happysad: But I can't get in without breaking the seal, or call poco.
Licensing requirements don't change the physics here.Is this house located in Cornwall, NY?
Best of luck!
Best of luck!
Don’t remember. If I go by I’ll check it out.No ground wire from meter base to the ground rod?
No other bonds to the meter base like telco or CATV?
At any rate, you need to add a neutral conductor. DIY by homeowner years ago? Can't imagine it being done by an EC.