Background: In the process of rewiring whole house, 200amp service panel, residential, 240V, 2 legs, 1 neutral, Florida, 4/0 cable into panel, smart meter, 1 ground rod directly below meter. I am not a residential electrician but that being said I have been to lots of electrical/Instrumentaiton and control schools. I dont understand everything so dont talk down to me like I see so many people do on forums. Just keep it informational and technical.
Problem: The voltage drops in my house have become excessive to the point where I cant even run a Playstation and Television set together from one outlet. Not sure about running them from opposite legs in the system. When the refrigerator compressor starts it drags down that leg.
I ussually read approximately 90V on one leg and 140V. The balance of leg fluctuations depending on loads starting and stopping. I can remove all breakers from my panel except one (not the neutrals and grounds for the circuits I remove though) and get voltage fluctions when trying both new and old type cirucits I wired.
240v Circuits seem to run balanced
Ive checked for tightness and found some loosed connections. I have tightened everything from the load side of the service breaker all the back to the utility side of the meter. I have checked connections of the grounding rod and wiring as well. I have checked the Neutral connection points all the back to the utility side of the meter.
Ive cut many wires and removed lots of different cirucits... possibly leaving improperly incompleted ciruicts on the neutrals and grounds.
Ive taken resistance reading from the utility side of the incoming wires all the way to my incoming service wires that connect to the 200amp service breaker and get about .5 Ohms
It seems like the more current Im drawing on an individual leg (the more unbalanced between the legs) the more mismatch in voltage... as if there is a high resistance connection at some point.
I am not super familiar with grounding practices (I understand a little bit) but what I understand is the ground rod is more safety and back up stabalization related than actual flow path since its at a much higher resistance but this may be the only path I have right now which would make since for the readings Im getting (High resistance and increasing currents equals higher imbalances and voltage drops.)
Ultimately it seems like Im completly missing the service neutral (No return path except for ground) It dont see any current flowing on my neutral. I havnt tested current on the grounding rod yet.... stray grounds are probably all over my house so not sure if the grounding rod will see all the current any way.
With some light lighting loads on my system when I measure voltages on the utility side of my meter I get the same imablances leading me to think that all the connection on my side are good.
Any thought or troubleshooting suggestions would be appreciated. If i left out any infomation please ask.
Thanks
Problem: The voltage drops in my house have become excessive to the point where I cant even run a Playstation and Television set together from one outlet. Not sure about running them from opposite legs in the system. When the refrigerator compressor starts it drags down that leg.
I ussually read approximately 90V on one leg and 140V. The balance of leg fluctuations depending on loads starting and stopping. I can remove all breakers from my panel except one (not the neutrals and grounds for the circuits I remove though) and get voltage fluctions when trying both new and old type cirucits I wired.
240v Circuits seem to run balanced
Ive checked for tightness and found some loosed connections. I have tightened everything from the load side of the service breaker all the back to the utility side of the meter. I have checked connections of the grounding rod and wiring as well. I have checked the Neutral connection points all the back to the utility side of the meter.
Ive cut many wires and removed lots of different cirucits... possibly leaving improperly incompleted ciruicts on the neutrals and grounds.
Ive taken resistance reading from the utility side of the incoming wires all the way to my incoming service wires that connect to the 200amp service breaker and get about .5 Ohms
It seems like the more current Im drawing on an individual leg (the more unbalanced between the legs) the more mismatch in voltage... as if there is a high resistance connection at some point.
I am not super familiar with grounding practices (I understand a little bit) but what I understand is the ground rod is more safety and back up stabalization related than actual flow path since its at a much higher resistance but this may be the only path I have right now which would make since for the readings Im getting (High resistance and increasing currents equals higher imbalances and voltage drops.)
Ultimately it seems like Im completly missing the service neutral (No return path except for ground) It dont see any current flowing on my neutral. I havnt tested current on the grounding rod yet.... stray grounds are probably all over my house so not sure if the grounding rod will see all the current any way.
With some light lighting loads on my system when I measure voltages on the utility side of my meter I get the same imablances leading me to think that all the connection on my side are good.
Any thought or troubleshooting suggestions would be appreciated. If i left out any infomation please ask.