150,000W / (480 x 1.732) = 180 amps
(1.732 x 21.2 x 180 x 2000) / 14.4 = 917,960mcm AL
(1.732 x 21.2 x 180 x 2000) / 14.4 = 917,960mcm AL
I noticed that. It's usually pretty close. I will have to investigate where you guys are screwing up.
That's a long run, is this in a commercial area, large residential? It might be cheaper depending on the clients needs to install a new service entrance and pole mounted xfmr closer to the load. If an option, utility companies normally have options for new meters where the startup cost is absorbed over time and or associated discounts.Looking at installing a panelboard to serve ~150 kW of load, but the only available and convenient voltage source nearby is 480... unfortunately it's about a 2,000' conduit run. The load is pretty variable so I can't look at things like capacitors for voltage support (unless it was automatically switched in/out?). I guess the obvious solution is to oversize the conductors to the point where voltage drop is 3% along the run, but I'm wondering if there's a better option? The only thing that comes to mind is a load tap changer on a 1:1 transformer, but not sure if those exist at the 480V level. Fishing for ideas, something I'm not aware of.
I know there have been some discussions in the past about significantly different results from different VD calculators......I used the southwire one should be more on the worst case side bc they sell wire and it assumes .9 power factor.
I noticed that. It's usually pretty close. I will have to investigate where you guys are screwing up.
If load remained constant, could possibly work. But remember you will have an overvoltage at no load/low load conditions.Can the first xformer be tapped a little higher so the voltage drops back to acceptable window after voltage drop?
Same here, but if you are boosting volts by 15 volts for VD compensation, that means if you start with no load volts of 500 it jumps to 515 with no load. May not cause immediate failure of anything but may not be helping life of certain components either.We frequently see 500 volts with no apparent ill effect on equipment.
We frequently see 500 volts with no apparent ill effect on equipment.
I had a large property where the running loads on the building during the day with 1700+ people, started bringing down the voltage on the secondary side of our 16kv/480v 2500 KVA Xfmr. As far down as 460vac. Our solution with the electrical companies blessing was to change the internal secondary tap on the transformer to D-Tap, this effort brought our daytime running voltage up to 480/485 vac.We frequently see 500 volts with no apparent ill effect on equipment.
Around here unloaded 480 volt services usually will run about 500 volts, 240 volt services about 250 and 208 services about 216 volts. Those are all within 5% of nominal.I had a large property where the running loads on the building during the day with 1700+ people, started bringing down the voltage on the secondary side of our 16kv/480v 2500 KVA Xfmr. As far down as 460vac. Our solution with the electrical companies blessing was to change the internal secondary tap on the transformer to D-Tap, this effort brought our daytime running voltage up to 480/485 vac.
When the Transformer was unloaded and everybody left for the day air handlers turned off big equipment not running the 500 volt output of the Transformer was closer to 499 when unloaded with a standard 5% impedance for a Transformer that size so yes to your comment about seeing 500 volts did not affect any of the critical UPS equipment or generator operation, gave us are 480 volts perfectly all the time when loaded.
Sent from my LGMP260 using Tapatalk
Sounds normal for totally unloaded, the property I was referring to had a minimum running load 24/7 of 1000 KW. Data center load plus cooling. So the building was never unloaded. I'm sure with no load on D tap it would have been much higher. Building loaded during the day was running at 1750kw [MENTION=63279]480[/MENTION]vac when dropped to 1000 at night it was up to 500 vac. So we used the buildings constant load + people load to maintain that range of 480/499.Standard deviation according to C84.1 for a 480Y/277V system is 504Y/291 (Max; service and utilization voltage) to 456Y/263V (min-service voltage) and 440Y/254V (min-utilization voltage)
Which corresponds to why transformers have standard taps of +/- 2 x 2.5% taps; i.e. 5% tap gets you to 504volts on a 480V system.
Intentionally boosting voltage makes sense if you are never unloaded to any significant level. What may be undesired is to do something to boost voltage so you see 490-500 while under full load but then end up with say 515 to 520 during periods of minimal load.Sounds normal for totally unloaded, the property I was referring to had a minimum running load 24/7 of 1000 KW. Data center load plus cooling. So the building was never unloaded. I'm sure with no load on D tap it would have been much higher. Building loaded during the day was running at 1750kw @480vac when dropped to 1000 at night it was up to 500 vac. So we used the buildings constant load + people load to maintain that range of 480/499.