kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
Switchgear, fuses, breakers, etc. no problem. That 480 x 120 volt control transformer is now putting out 133 volts, and may be supplying some loads that are on even though the major loads are currently off. Though that may be around the upper end of what may be acceptable, this only gets worse if the 480 volt nominal supply goes up to around 500 when load is minimal, then that extra 10% gets closer to 550 volts, and the 120 volt control transformer may be closer to 145.Equipment at 480V is rated for 600V. What is going to be the problem if you are 10% above at 528V unloaded.