I am running 4/4/4/2 urd in 1.5” pvc conduit direct burial. Can I run 4 #14 stranded thhn in the same pipe for a switch leg ?
I am running 4/4/4/2 urd in 1.5” pvc conduit direct burial. Can I run 4 #14 stranded thhn in the same pipe for a switch leg ?
If this is a feeder-- yes. If these are service cables-noI am running 4/4/4/2 urd in 1.5” pvc conduit direct burial. Can I run 4 #14 stranded thhn in the same pipe for a switch leg ?
The underlying principle is that service conductors are not effectively protected by upstream OCPD but rather are just expected to burn out in a bad enough fault condition. So mixing them in a raceway with protected circuits would potentially defeat that protection, which would be a bad thing.If this is a feeder-- yes. If these are service cables-no
Dennis, thanks for your response, the quad is a sub feed from my combo meter/ panel . For a small shop.all down line from meter.If this is a feeder-- yes. If these are service cables-no