We had a Contractor move on site and installed a Temporary Mobile Home to work out of. The EC ran a conduit to an electrical panel about 50' away. The breaker is a 2 pole that matches the MH panel main. My question is should the EC install a service disconnect within 30' and drive a ground rod or since he's within line of sight of the MH just install a ground rod adjacent the MH and run a GEC from the MH main panel inside. After reading definition "structure" and 250.32, 250.50, and 550.32 I am confused. Need insight! Thanks!!
I am assuming temporary.
Read these two and see if this helps.
590.2 All Wiring Installations.
(A) Other Articles. Except as specifically modified in this
article, all other requirements of this Code for permanent
wiring shall apply to temporary wiring installations.
550.4 General Requirements.
(A) Mobile Home Not Intended as a Dwelling Unit. A
mobile home not intended as a dwelling unit ? for example,
those equipped for sleeping purposes only, contractor?s
on-site offices, construction job dormitories, mobile
studio dressing rooms, banks, clinics, mobile stores, or intended
for the display or demonstration of merchandise or
machinery ? shall not be required to meet the provisions
of this article pertaining to the number or capacity of circuits
required. It shall, however, meet all other applicable
requirements of this article if provided with an electrical
installation intended to be energized from a 120-volt or
120/240-volt ac power supply system. Where different voltage
is required by either design or available power supply
system, adjustment shall be made in accordance with other
articles and sections for the voltage used.
Now is it a mobile home or a manufactured home?