My main reason for not accepting it is that it is not true.
It can reduce the overall impedance between the GEC and the POCO transformer secondary, but it does that only by its effect on the secondary to earth resistance and cannot reduce the overall resistance in the circuit below the resistance between the ground rod and remote earth.
If you present your objection with a diagram or calculation, it will be very helpful.
The other ground electrodes connected to the neutral are in parallel with the ground rod at the customer side through GEC. Correct?
If yes, then if you measure the earth resistance of the rod without disconnecting the GEC, then the earth resistance of rod would be the equivalent resistance of all the parallel resistances of ground electrodes connected to the neutral. Correct?