Senior Member
I'm not that convinced that "approved" equipment is all that necessary as they are fancy voltage and current meters. What in the world did we do before the fancy equipment was available?As for taking an earth resistance measurement, I don't necessarily have the "approved" equipemnt to do that. I did go outside today and do some more testing.
You have the means to run a current (I) through the ground. Now run the current between two ground rods with a separation of at least 60X the rod depth. Drive two more rods in a line between the current rods at a separation of A cm, keeping the rods evenly spaced, and measure the voltage drop (V) in the soil. Be sure the rod separation for all of the rods is at least 20X greater than the rod depth (i.e. 4 rods => 3 spaces => 3 spaces * 20X separation = 60X separation end-to-end).
The ohms resistance (R) is V/I. The soil resistivity (r) in ohm-cm to the depth of your rods is: r = 2*Pi*A*R