You have to run the numbers.
I ran a model for a 1 mile 115 kV transmission line with a 0.0001 ohm N-E connection to remote earth on the source end. Beyond that, I ran a 20 mile transmission line with a 0.0001 ohm N-E connection to remote earth at the source and load end. In the 20 mile section, I paralleled the earth with a giant conductor to short the earth resistance during a fault for case #1. For case #2 I then opened the parallel conductor to run fault current through earth only.
If the earth is a perfect conductor, then we would expect most of the current to be in the earth instead of in the parallel path. But that is not the reality of how currents run through the transmission line and earth.
The fault I created was a A-N fault at the end of the 21 miles. Clearly the earth path is resisting the current even though we have a negligible connection resistance to remote earth.
With parallel path:
In the 20 mile section:
Phase A: 590 amps
parallel path: 395 amps
earth: 196 amps
In the 1 mile section:
Phase A: 590 amps
earth: 590 amps
Without parallel path:
In the 20 mile section:
Phase A: 430 amps
earth: 430 amps
In the 1 mile section:
Phase A: 430 amps
earth: 430 amps