mayanees
- Westminster, MD
- Electrical Engineer and Master Electrician
Follow-up on this .....
Motor was returned this morning; they said it had some issues they fixed along with replacing the motor starter and heaters. I was told the capacitors I installed are the right size.
So this motor has a legit starting current of 255A. I had a 60A cb on this circuit and it won’t hold. I connected directly to the line side of the incoming feeder unfused, and after 6 seconds of 255A, it dropped to 40A.
The nameplate on the blower calls for a 45A circuit. Never seen this in my life.
I just ordered some sub-feed lugs for the loadcenter to see if it will hold on the 200A MCB.
I think you need a 150-amp breaker, per Table 430.52, with the option of going as high as 400% of 55 = 220 (200) per exception 2c if the 150 doesn't hold.