Hello,
I have a question that I haven't been able to get my mind around.
When protecting motor circuits we design both for short circuit (over current) and over load. Each has different requirements per NEC. If I have a panelboard that supplies one motor, how do I determine the size of the breaker via Short ckt propetection or over load protection? To elaborate further, the motor would be installed on the roof, and the panel board is on the floor below.
Assumming a Design B, 15 hp, 208V three phase squirrel cage motor with a 1.15 service factor. Nameplate current of 40.2 A and dual element fused disconnect switch for short circuit in weather proof enclosure.
Per table 430.250, the rated current is 46.2A. Per table 430.52 the sc setting would be 80.85A, we could then fuse it at 90A.
How to size the feeder coming from the panel board? Per 430.62 the feeder sc circuit protection shall not exceed the rating of the highest short circuit protection plus any additional loads. The handbook states that it is assumed the same type of proptective device is used. So, if I was protecting the feeder with another fused disconnect I would not have any confussion on the matter, it should not exceed 90A. Since I am using an inverse time breaker instead, how is it evaluated?
Are we to take 430.62 on a relative term? Meaning, if table 430.52 calls for 175%for dual element fuses and 250% for inverse time breakers, are we to "transform" the fused disconnect rating to its corresponding inverse time breaker and size the feeder protection accordingly? In this particular example, the 90A dual element fuses would have been 125A on an inverse time breaker. So my feeder protection breaker should not exceed 125A.
Or, as we to take 430.62 literally? On this example, with the 90A fuses, my breaker shall not exceed 90A. But since the short circuit requirement difference between these two devices is due to their ability to withstand the inrush current, am I risking the breaker to open during inrush?
Which one is it? Any thoughts?
Thanks.
Jose
I have a question that I haven't been able to get my mind around.
When protecting motor circuits we design both for short circuit (over current) and over load. Each has different requirements per NEC. If I have a panelboard that supplies one motor, how do I determine the size of the breaker via Short ckt propetection or over load protection? To elaborate further, the motor would be installed on the roof, and the panel board is on the floor below.
Assumming a Design B, 15 hp, 208V three phase squirrel cage motor with a 1.15 service factor. Nameplate current of 40.2 A and dual element fused disconnect switch for short circuit in weather proof enclosure.
Per table 430.250, the rated current is 46.2A. Per table 430.52 the sc setting would be 80.85A, we could then fuse it at 90A.
How to size the feeder coming from the panel board? Per 430.62 the feeder sc circuit protection shall not exceed the rating of the highest short circuit protection plus any additional loads. The handbook states that it is assumed the same type of proptective device is used. So, if I was protecting the feeder with another fused disconnect I would not have any confussion on the matter, it should not exceed 90A. Since I am using an inverse time breaker instead, how is it evaluated?
Are we to take 430.62 on a relative term? Meaning, if table 430.52 calls for 175%for dual element fuses and 250% for inverse time breakers, are we to "transform" the fused disconnect rating to its corresponding inverse time breaker and size the feeder protection accordingly? In this particular example, the 90A dual element fuses would have been 125A on an inverse time breaker. So my feeder protection breaker should not exceed 125A.
Or, as we to take 430.62 literally? On this example, with the 90A fuses, my breaker shall not exceed 90A. But since the short circuit requirement difference between these two devices is due to their ability to withstand the inrush current, am I risking the breaker to open during inrush?
Which one is it? Any thoughts?
Thanks.