Motor circuit

Status
Not open for further replies.

nickelec

Senior Member
Location
US
How would you guys size the circuit for this motor I'm coming up with #10s on 40a breaker
46b5203bb0017eb25ccdaec7274296fa.jpg
0ec376155c6b84970d677398bb3f6680.jpg


Sent from my SM-S906U using Tapatalk
 
It's 10 hp. At 460 V, that's 14 A per NEC. 1.25 x 14 = 17.5 A. Conductors have to be rated 17.5 or higher. Molded case breaker should be 25 A. In theory #14 AWG would work if rated 75 deg C (along with terminations). #12 AWG is probably better.
 
Per NEC, it would be a 35 amp breaker (430.52 @ 14amp). The chart seems to indicate it might be called upon to run at 1.;25% so I would lielly go with a 12 minimum (albeit a 14 meets Code).
 
Ty all but here in the great city of NY #14 is illegal it's #12 minimum

Sent from my SM-S906U using Tapatalk
 
Status
Not open for further replies.