delta starting torque 150% x rated torque
wye ~ 1/3 of that or 50%
if torque required to start > 50% of rated fl torque motor may stall
this may occur with some machines, conveyors, hoists, elevators
There's the answer I think you were looking for tariqzia.
Current and torque are basically the same in terms of percentages and vary by the square of the voltage difference. So if you you use Start-Delta starting, or just permanently connect a motor in Star when it was supposed to be Delta, the effect is the same. The EFFECTIVE voltage across the coils in Star will be lower by the sq. root of 3, so divided by 1.732 (or multiplied by the inverse, 57.7%). Applying the torque formula to that then means the torque and thereby current, becomes .577 squared or 33.3% (1/3) of the torque/current at the designed voltage. That carries through to the starting torque/current as Ingeniuer pointed out.
So yes, you will reduce your current to 1/3, but you ALSO reduce your peak torque capability to 1/3 as well. Peak torque is what your motor uses to accelerate and also RE-accelerate a motor after a change in load. Without the same torque available from the motor,
if your LOAD connected to the motor is not also reduced to 1/3, then the slip increases, the motor draws more current, and if it cannot accelerate or even run the load with that increased torque/current, it will overload and go off line (hopefully) or burn up.
Side note that I'm thinking MIGHT be the basis of your question:
If you DO happen to have a motor that is
3x the size necessary for the load connected to it, then you can reconnect it in Star permanently. This is done in a lot of developing countries where old large industrial facilities are repurposed and the new purpose is significantly lower. I see this happen a lot in India for example (through connections I have there, I've never been there) so I can imagine that Pakistan has similar issues going on. The reason they do this is because in a motor, there is a certain amount of fixed energy used in just turning the coils and steel into magnets, and a portion of that portion of the energy used on that is lost due to things like eddy currents in the steel. These are called the "core losses" and vary directly with the applied voltage. So by reconnecting a motor in Star where it becomes 57.7% of the effective coil voltage, the core losses are reduced to 57.7% as well. Again, this represents a fraction of a fraction of a fraction of the total motor energy used so the risk/reward ratio is very low. But in some places they feel it's worth it.