Current and torque are basically the same in terms of percentages and vary by the square of the voltage difference. So if you you use Start-Delta starting, or just permanently connect a motor in Star when it was supposed to be Delta, the effect is the same. The EFFECTIVE voltage across the coils in Star will be lower by the sq. root of 3, so divided by 1.732 (or multiplied by the inverse, 57.7%). Applying the torque formula to that then means the torque and thereby current, becomes .577 squared or 33.3% (1/3) of the torque/current at the designed voltage. That carries through to the starting torque/current as Ingeniuer pointed out.
So yes, you will reduce your current to 1/3, but you ALSO reduce your peak torque capability to 1/3 as well. Peak torque is what your motor uses to accelerate and also RE-accelerate a motor after a change in load. Without the same torque available from the motor, if your LOAD connected to the motor is not also reduced to 1/3, then the slip increases, the motor draws more current, and if it cannot accelerate or even run the load with that increased torque/current, it will overload and go off line (hopefully) or burn up.
I 100% agree with Jraef. Let me give another example.
I was called from 200 miles away to troubleshoot an injection molding machine that had been misbehaving for 2 years since being commissioned. The OEM had replaced the motor, pump, motor starter and verified all wiring.
Machine would start and run ok for hours, days or weeks, then trip the overloads.
Turns out the OEM had designed for use in applications where wye-delta starting was needed, but this plant ordered for across-the-line start. Only 3 wires from the motor ... connected in wye. The pump was unloaded for start, so probably only 15% or so of full load torque was needed to start.
We never learned why it sometimes tripped; my money is on either operator settings or intermittent slightly low voltage. I made them open the motor terminal box ... they were SURE it was correct ... swapped the jumpers on the motor (what I call European style with 6 binding posts and either 2 or 3 jumpers) to delta and all was fine; they said it seemed to start too fast<g>.
I was asked how I knew ... told the truth, just logical troubleshooting, didn't know. OEM fumed at being back charged for downtime and multiple service calls. My employer was asked to send me in 3 more times to provide training.
My philosophy ... keep an open mind, and everyone lies even when they don't know they are lying.