texie
Senior Member
- Location
- Fort Collins, Colorado
- Occupation
- Electrician, Contractor, Inspector
I'm struggling for the correct MCC bus/MCC main breaker size for the load below:
2 each 100 HP 480 motors. Table value of 124 amps each. There is also 53 amps of other misc. calculated load fed by the MCC.
Each motor is VFD with a nameplate input of 156 amps. Each VFD has a 200 amp inverse time breaker in the MCC.
Method 1: 124 amps + 200 amps = 324 + 53 = 377 (400 amp breaker/bus).
Method 2: 156 amps + 200 amps = 356 + 53 = 409 (600 amp bus/450 or larger main breaker).
The real issue here is whether method 1 is NEC compliant as if not the the next standard MCC bus sizing is 600 and adds a great deal of cost.