I'm struggling for the correct MCC bus/MCC main breaker size for the load below:
2 each 100 HP 480 motors. Table value of 124 amps each. There is also 53 amps of other misc. calculated load fed by the MCC.
Each motor is VFD with a nameplate input of 156 amps. Each VFD has a 200 amp inverse time breaker in the MCC.
Method 1: 124 amps + 200 amps = 324 + 53 = 377 (400 amp breaker/bus).
Method 2: 156 amps + 200 amps = 356 + 53 = 409 (600 amp bus/450 or larger main breaker).
The real issue here is whether method 1 is NEC compliant as if not the the next standard MCC bus sizing is 600 and adds a great deal of cost.
430.94 Overcurrent Protection. Motor control centers shall
be provided with overcurrent protection in accordance with
Parts I, II, and VIII of Article 240. The ampere rating or
setting of the overcurrent protective device shall not exceed
the rating of the common power bus. This protection shall be
provided by (I) an overcurrent protective device located ahead
of the motor control center or (2) a main overcurrent protec-
tive device located within the motor control center.