Why wouldn't you size the overcurrent protective device based on 430.62 and then add the miscellaneous loads.
Why wouldn't you size the overcurrent protective device based on 430.62 and then add the miscellaneous loads.
Read it carefully. It does not say it implies more than one motor. Paraphrased, it says one or more VFD-controlled motor, possibly other motors, and perhaps other loads. Total net minimum one VFD controlled motor. One load does not constitute the need for a feeder... but the conductors can be a feeder all the same.It does not imply more than 1 motor
no more than 'feeder' does in fig 430.1
which references part II 430.22
The 156 (or 155) is already factored 125%. Motor loads are 124A each.I would size it 1.25 x 156 + 156 + 1.25 x 53 = 418
in reality based on likelyhood of expansion 600 to a 600 mcc
You're elected to write it up.this would be a good one to submit to the nec for written clarification
What about It? 430.122 has no mention of the other loads.What about the additional 53 amps of "other misc" for the second calculation?
Read it carefully. It does not say it implies more than one motor. Paraphrased, it says one or more VFD-controlled motor, possibly other motors, and perhaps other loads. Total net minimum one VFD controlled motor. One load does not constitute the need for a feeder... but the conductors can be a feeder all the same.
The 156 (or 155) is already factored 125%. Motor loads are 124A each.
You're elected to write it up.
After rereading the OP, you are correct in that 156A is the VFD rated input current.I read everything carefully (thoughtfully?)
otherwise why read it
you are seeing something others are not
the sizing imo is the same as multiple motors using vfd rated current rather than motor fla
the vfd 156 is not motor fla x 125%
it is the max input i, it can vary with drive
the 125% is still applied the the vfd input i regardless
430.122 Conductors — Minimum Size and Ampacity.
(A) Branch/Feeder Circuit Conductors. Circuit conductors
supplying power conversion equipment included as
part of an adjustable-speed drive system shall have an ampacity
not less than 125 percent of the rated input current to
the power conversion equipment.
After rereading the OP, you are correct in that 156A is the VFD rated input current.
Seems David Kuchini sees it as I do. What
The power conversion equipment has a combined rated input current of:
156 + 156 = 312A.
Factored:
125% × 312 = 390A
The section doesn't say we have to add other loads, but the feeder circuit conductor ampacity cannot be less than 390A.
That's one person's opinion. It's not even Charlie Trout answering anymore. He passed back in October 2015.Not accurate
http://www.neca-neis.org/code-question-of-the-day/code-question/cqd-for-3-10-2011
Where multi-motor installations have individual drives, each drive should be sized for the individual motor. The branch circuit conductors supplying the power conversion equipment for the multi-motor power conversion equipment should be sized according to 430.24.
Indeed. I don't understand why you would need to "interpret" what the section says rather than following the plain language of the text.The section doesn't say we have to add other loads, but the feeder circuit conductor ampacity cannot be less than 390A.
That's one person's opinion. It's not even Charlie Trout answering anymore. He passed back in October 2015.
What about It? 430.122 has no mention of the other loads.
It isn't supplied by an adjustable speed drive but the feeder in question is still supplying 53 amps of additional unspecified load.What about It? 430.122 has no mention of the other loads.
It isn't supplied by an adjustable speed drive but the feeder in question is still supplying 53 amps of additional unspecified load.
It addresses "power conversion equipment." For a feeder, this may be a single vfd or it may be multiple vfd's.because it only addresses a single vfd
See post #5for multiple vfd/motors and other misc loads 430.24 applies since it is not addressed in X
Where one or more VFD's are involved, compliance with both 430.24 and 430.122 are required... not one or the other. You cannot ignore 430.122 simply because a branch or feeder circuit supplies more than one VFD... at least not how it is currently worded. If you believe, for multi-motor, multi-VFD applications, ampacity should be determined using 125% of the greater of the largest motor or VFD input current rating according to 430.24, then, by all means, propose it for the next iteration of Code.because it only addresses a single vfd
for multiple vfd/motors and other misc loads 430.24 applies since it is not addressed in X
so if a feeder supplies 2 1 hp drives and a 10 kw heater only the vfds need considered when sizing?
more proof that 430.24 applies
Where one or more VFD's are involved, compliance with both 430.24 and 430.122 are required... not one or the other. You cannot ignore 430.122 simply because a branch or feeder circuit supplies more than one VFD... at least not how it is currently worded. If you believe, for multi-motor, multi-VFD applications, ampacity should be determined using 125% of the greater of the largest motor or VFD input current rating according to 430.24, then, by all means, propose it for the next iteration of Code.
Where one or more VFD's are involved, compliance with both 430.24 and 430.122 are required... not one or the other. You cannot ignore 430.122 simply because a branch or feeder circuit supplies more than one VFD... at least not how it is currently worded. If you believe, for multi-motor, multi-VFD applications, ampacity should be determined using 125% of the greater of the largest motor or VFD input current rating according to 430.24, then, by all means, propose it for the next iteration of Code.
wrong
122 tells you how to size the conductor for a single conversion device (as opposed to conventional starting methods and 1 motor), use the input I rating
24 tells you how to deal with multiple devices
I don't need to propose it, that is already code
Calculate the minimum feeder ampacity from 430.24, then calculate the minimum feeder ampacity from 430.122.
The larger value is your minimum feeder ampacity.
Wrong.
122 tells you how to size conductors supplying "power conversion equipment." Nowhere does it state that it applies to conductors for a single conversion device.