Journeyman Exam Question:
1.) If a single-phase motor draws 50 Amperes and its branch circuit is protected by a 150-ampere nontime-delay fuse, the feeder overcurrent protective device may not be larger than:
A.) 87.5 amperes C.) 300 amperes
B.) 100 amperes D.) 150 amperes
Answer: D.) 150 amperes ART. 430.62(A.)
Follow-up Question:
If you size the feeder to 125% of the motor FLA, this gives you ,at 75Celsius, a #6 AWG conductor. A #6 AWG is rated for 65 Amperes.
For feeders with a long length, what is protecting the conductors in between the 150A feeder OCPD and the fusible disconnect(150A nontime-delay fuse)?