Section 430.62 is for feeder short circuit and ground fault protection for motors. I'm getting mixed up on definitions here. This section assumes that feeder conductors supplying motors are tapped. Then the protection for the feeder is the largest protection of the largest motor plus the sum of the remaining motor FLCs.
Article 100 defines a feeder as the conductors from the service entrance equipment to the branch circuit OCPD. So if you have a 42 pole branch circuit panel, the feeder conductors would be the conductors coming into the panel and the branch circuit conductors would be for each circuit breaker.
The rule in section 430.62 for sizing feeder protection of motors doesn't make sense for a panelboard with motors on branch circuit circuit breakers. For instance, the feeder OCPD wouldn't be 20A + 5A + 5A for a 200A panel with 3 motors on the branch circuits. Am I missing something?
Article 100 defines a feeder as the conductors from the service entrance equipment to the branch circuit OCPD. So if you have a 42 pole branch circuit panel, the feeder conductors would be the conductors coming into the panel and the branch circuit conductors would be for each circuit breaker.
The rule in section 430.62 for sizing feeder protection of motors doesn't make sense for a panelboard with motors on branch circuit circuit breakers. For instance, the feeder OCPD wouldn't be 20A + 5A + 5A for a 200A panel with 3 motors on the branch circuits. Am I missing something?