Alwayslearningelec
- NJ
- Estimator
If a motor on the drawing shows a homerun 3#12 & 1#12 ground or 3#8 & 1#10 ground is the ground wire needed. I though the conduit could be used as a ground? THanks.
You have to quote and install based on the design even where that design exceeds the minimum requirements of the NEC.If a motor on the drawing shows a homerun 3#12 & 1#12 ground or 3#8 & 1#10 ground is the ground wire needed. I though the conduit could be used as a ground? THanks.
You could just use an equipment bonding jumper around the flex and not have to install an EGC of the wire type in the complete raceway.Since you won't be connecting a solid raceway to the motor and flexibility is usually required then the raceway must contain a wire type EGC.
I am not aware of grounding connectors for FMC like they have for LFMC, but you can just use a clamp on the conduit and a connection to the motor with a lug.I agree. And EGC in the raceway would be just one of many code compliant methods. A bonding jumper would be another. If FMC is used for flexibility some wire type of EGC/bonding jumper is required. I don't know of a readily available fitting that allows a bonding jumper to be installed around the outside of FMC.
Flexible conduit COULD contain a grounding provision that will provide grounding continuity of the rigid conduit if connected with appropriate connectors on both end. External bonding jumper can also be used.Since you won't be connecting a solid raceway to the motor and flexibility is usually required then the raceway must contain a wire type EGC.