If a motor on the drawing shows a homerun 3#12 & 1#12 ground or 3#8 & 1#10 ground is the ground wire needed. I though the conduit could be used as a ground? THanks.
You have to quote and install based on the design even where that design exceeds the minimum requirements of the NEC.If a motor on the drawing shows a homerun 3#12 & 1#12 ground or 3#8 & 1#10 ground is the ground wire needed. I though the conduit could be used as a ground? THanks.
You could just use an equipment bonding jumper around the flex and not have to install an EGC of the wire type in the complete raceway.Since you won't be connecting a solid raceway to the motor and flexibility is usually required then the raceway must contain a wire type EGC.
Since you won't be connecting a solid raceway to the motor and flexibility is usually required then the raceway must contain a wire type EGC.
Since you won't be connecting a solid raceway to the motor and flexibility is usually required then the raceway must contain a wire type EGC.
You could just use an equipment bonding jumper around the flex and not have to install an EGC of the wire type in the complete raceway.
You could just use an equipment bonding jumper around the flex and not have to install an EGC of the wire type in the complete raceway.
I am not aware of grounding connectors for FMC like they have for LFMC, but you can just use a clamp on the conduit and a connection to the motor with a lug.I agree. And EGC in the raceway would be just one of many code compliant methods. A bonding jumper would be another. If FMC is used for flexibility some wire type of EGC/bonding jumper is required. I don't know of a readily available fitting that allows a bonding jumper to be installed around the outside of FMC.
Flexible conduit COULD contain a grounding provision that will provide grounding continuity of the rigid conduit if connected with appropriate connectors on both end. External bonding jumper can also be used.Since you won't be connecting a solid raceway to the motor and flexibility is usually required then the raceway must contain a wire type EGC.