hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have motor operated appliance whose manufacturer install instruction does Not mark overcurrent protection size and it is also Not marked on appliance.
I am trying to figure out in NEC 2014 how to size branch circuit breaker in panelboard to the motor operated appliance which does Not mark overcurrent protection in instruction or does not mark on appliance.
I looked at NEC 2014 Section 422.11 which says appliance shall be protected against overcurrent in accordance with 42.11(A) to 422.11(G).
NEC 2014 section 422.11(A) first paragraph says branch circuit shall be protected in accordance with 240.4. When I look at 240.4 it is not clear if 240.4(A) or 240.4(G) apply. Also if 240.4(G) applies then table 240.4(G) points back to part II of 422 which then goes back to 422.11 and goes in cycle without know how to size branch circuit breaker.
Does anyone know how to size branch circuit breaker in panelboard to the motor operated appliance which does Not mark overcurrent protection in instruction or Not mark on appliance according to NEC 2014?
I am trying to figure out in NEC 2014 how to size branch circuit breaker in panelboard to the motor operated appliance which does Not mark overcurrent protection in instruction or does not mark on appliance.
I looked at NEC 2014 Section 422.11 which says appliance shall be protected against overcurrent in accordance with 42.11(A) to 422.11(G).
NEC 2014 section 422.11(A) first paragraph says branch circuit shall be protected in accordance with 240.4. When I look at 240.4 it is not clear if 240.4(A) or 240.4(G) apply. Also if 240.4(G) applies then table 240.4(G) points back to part II of 422 which then goes back to 422.11 and goes in cycle without know how to size branch circuit breaker.
Does anyone know how to size branch circuit breaker in panelboard to the motor operated appliance which does Not mark overcurrent protection in instruction or Not mark on appliance according to NEC 2014?