InjunEar...
1.2A is the Line-current! The motor's NLA is still 10.4! It does not change!!!
Phil
What do you think the CT is measuring?
at the motor
or the controller, ie line
Pretty much the crux of the op's ???
w/o cap 10
with zilch
InjunEar...
1.2A is the Line-current! The motor's NLA is still 10.4! It does not change!!!
Phil
I have to admit that I skimmed through ths but one thing occurs to me.
If it's a motor protection relay it ought to be looking at just motor current. Not motor plus PFC. Strikes me that it is in the wrong place if it sees both.
I have to admit that I skimmed through ths but one thing occurs to me.
If it's a motor protection relay it ought to be looking at just motor current. Not motor plus PFC. Strikes me that it is in the wrong place if it sees both.
Why is that? Do you think a fault in the motor will potentially not be seen by the relay because of the PFC?
The idea of a motor protection relay is to protect the motor. The motor will be damaged by a certain current level integrated over time, regardless of the power factor of that current.
It is a bit of a stretch, but consider a motor which is frequently started and intermittently overload for a longer period of time. An overcurrent device may allow the motor to continue in use based on the fact that it is cooling off between uses.
But if the current in the motor is 10A between uses it will not cool off as fast as if the current is 1A. The relay is operating with insufficient information.
It is not clear to me whether the relay in question is a full current over time overload device or just an overcurrent detection device with a long enough time delay to allow starting. If the latter, then there is still the problem that at full load with a PF of .9 the relay may read 90A when the actual current is 100A. Since losses are I2R dependent, a 10% difference in I makes a 20% difference in heat.
The lower the full load PF of the motor the worse the problem is, and PF compensation is more likely to be needed on a motor with low PF.
Or the motor protection realy might register a fault on the PFC but the motor is fine.Why is that? Do you think a fault in the motor will potentially not be seen by the relay because of the PFC?
Nailed it in one!The idea of a motor protection relay is to protect the motor.
You might find this interesting.
http://www.eaton.com/ecm/groups/public/@pub/@electrical/documents/content/sa02607001e.pdf
Page 16 shows the choices of where to put the caps, replace the overloads with a Multilin & associated CT's.