I agree it would be thermal trip and not instantaneous trip, now if the motor would at least turn it may not trip or at least current would start dropping as speed increased and maybe a 80 to 100 amp breaker holds long enough to get the motor accelerated.
Sorry for the blackout... We were not able to measure voltage during humming of motor (I would have liked to see the value).
I asked to wire the transformer in delta-delta so we can feed 240V to the hydraulic unit. With voltage drop calculated we should be seeing a minimum of 230V for running operation.
The hydraulic unit worked as intended, the motor was able to start under pressure with now problem.
To answer Jraef's question about relieving the pressure, this unit does not do that, most hydraulic units or air compressors I've seen normally do, but this one does not have any automatic means to do so before starting the motor.
I've asked to the electrician to not use the panel and instead feed power to a MCCB breaker with adjustable trip so we can increase to 90A or so... Cable would remain the same since it's a 90C and per NEC it is rated for 75A. So a 20HP at 230V has a FLC of 59.4 per NEC table.... 125% of 59.4A = 74.25A
Overload is set to 75A per vendor, do still thing is too high. Vendor mentioned running current is 60 to 70amps when motor is under load.... Huh? I would ask vendor to confirm skid is under warranty with the overload setting being above safety values. Any comments on the overload?
Thanks,