Thanks templdl...
We won't be installing a QP, it would be a Cutler Hammer MCP on a separate panel.
As for the voltage drop, we would have a lower drop due to less cable impedance, at the moment it would be less than 3%. We are supplying 240V for a 230V motors. So I think we are good with that.
I have one other problem...:weeping:
This is what happens you get asked to get involved after the fact everything has been installed and vendor mentions motor is 15HP instead of 20HP. Is this reverse engineering?
The transformer feeding the motor is a 30KVA 4.39% with a secondary current of 72.25A. Calculating voltage drop due to motor inrush is.... high. Nema B motor, inrush about 6xFLA... so 48*6 = 288A divided by sec current (72.25A) times impedance %, it gives me a voltage drop of 17.5%. :rotflmao:
Trying to see what to do...
Installing an Eaton MCP in a stand alone enclosure? Feed by what and from what location? What ever possesed whomever the an MCP would bring anything to the party? If you knew anything about an MCP it is a reverse UL component listed device. TTY o purchase one, which you can do, as if it is 150a continuously rated or less it is the same dimensions as the F-frame series C breakers. BUT it is a violation of its UL listing ás well as a NEC violation!
Thinking that were were close to addressing your application issues now you have thrown a wrench back into the gears.