We are a company that installs about 6000 single gang NEMA 3R boxes a year in an outdoor location on roofs. We work in over 70 cities and one city's AHJ inspector is stating that we cannot mount our metal j-boxes by using self-tappers with a EPDM washer since it voids the UL listing of the box by modifying it.
This seems to be inconsistent with the other 70 cities building departments since it is acceptable to them. In fact, NEC 314.15 provides for drilling weep holes in J-boxes to let moisture out which if that is the case, then that would also violate the UL.
Can anyone tell us a way , or code, to inform this inspector that it is perfectly acceptable for us to install j-boxes in this way? Thank you. The jbox is the die cast aluminum 5323-0 single gang.
UL file 195978 SA C22.2 No 18
The Self-tapping Screw with Neo0EPDM washer is type BSD = SAE J78-2013
Thanks
This seems to be inconsistent with the other 70 cities building departments since it is acceptable to them. In fact, NEC 314.15 provides for drilling weep holes in J-boxes to let moisture out which if that is the case, then that would also violate the UL.
Can anyone tell us a way , or code, to inform this inspector that it is perfectly acceptable for us to install j-boxes in this way? Thank you. The jbox is the die cast aluminum 5323-0 single gang.
UL file 195978 SA C22.2 No 18
The Self-tapping Screw with Neo0EPDM washer is type BSD = SAE J78-2013
Thanks