glene77is
- Memphis, TN
Guys,
Cautionary Example !
Came across a Kitchen Circuit, for Dishwasher/Disposal and Kitchen Countertop.
with 240 V on the Countertop Recepticals.
Wired as MWBC, from the Loadcenter to the first Countertop Receptical, then on to the D/D.
Ckt #1 fed the Countertop.
Ckt #2 fed the D/D with Switch on Disposal.
Neutral was "shared" at this junction, and the joint was on the Receptical.
The MWBC fed into the junction box for the Countertop Receptical FIRST,
and then Ckt #2 fed down to the D/D.
The home-run neutral was broken free from the Countertop Receptical.
The Countertop Receptical was used for the neutral joint connection.
Thus the MWBC circuit appeared to be "dead", but was reading 240V.
The Countertop appliances were throwing sparks when turned on.
The Dishwasher had been zapped by the 240V and was not working, and was unplugged.
The Disposal was actually in working order, but without proper power.
The Disposal Switch was in working order, and had been left "ON".
Thus, with the Disposal Switch turned "ON"
the power ran from Phase Ckt #2 directly to the D/D junction box and D/D receptical,
up to the Disposal Switch, back down to the Disposal,
through the Disposal, and out the Disposal neutral.
The neutral carried this power back to the CounterTop Receptical.
Since the Home Run was broken free at the Countertop Receptical,
there was NO Neutral Return.
There was 240V on the Receptical by having both MWBC phases on the Receptical.
Fix:
Wire the MWBC Neutral system as a "Back-Bone" ALWAYS,
just as the current code specifies.
Checked other portions of his house.
This house has "push-in" wired recepticals everywhere.
This house has this same loose wire problem everywhere.
The house owner is unable to comprehend this problem,
and unwilling to accept the prescribed 'fix' of replacing every receptical in the house.
Fixed his kitchen receptical as a deadly safety hazard, and said "good-bye".
Fix: