Having a 3 pole, 20 amp breaker, is it legal to install #12 on two poles and #10 on the other?
Yes. But if the circuits share a common neutral, then it has to be #10. Also, if they share a common EGC, it also has to be #10.
Now that I have typed that, I am suddenly uncertain about the sentence that starts with "but if." I don't want to withdraw it, but I am not sure the code would back up my claim. What do you all think: Can you have a #10 ungrounded and a #12 grounded on a 20 amp circuit? :?
Yes. But if the circuits share a common neutral, then it has to be #10. Also, if they share a common EGC, it also has to be #10.
Now that I have typed that, I am suddenly uncertain about the sentence that starts with "but if." I don't want to withdraw it, but I am not sure the code would back up my claim. What do you all think: Can you have a #10 ungrounded and a #12 grounded on a 20 amp circuit? :?
Since this is a 20 amp circuit I see no reason why you would need a #10 neutral. I agree with you on the EGC.
The neutral must be a 10 as well. If you increased for voltage drop they must increase as well and also isn't the neutral required to be at least the size of the ground wire?? making it a 10 also.
Having a 3 pole, 20 amp breaker, is it legal to install #12 on two poles and #10 on the other?
I see the logic but can you cite a code section that makes this a requirement?
Having a 3 pole, 20 amp breaker, is it legal to install #12 on two poles and #10 on the other?
Yes. But if the circuits share a common neutral, then it has to be #10. Also, if they share a common EGC, it also has to be #10.
Now that I have typed that, I am suddenly uncertain about the sentence that starts with "but if." I don't want to withdraw it, but I am not sure the code would back up my claim. What do you all think: Can you have a #10 ungrounded and a #12 grounded on a 20 amp circuit? :?
I cannot find a reference but I really want to say no. Somewhere I am hoping that there is something like 215.2(A)(2) for a branch circuit and then I can apply 250.122(B) to the grounded conductor.
(2) Grounded Conductor. The size of the feeder circuit
grounded conductor shall not be smaller than that required
by 250.122.....
Wow using a requirement for the EGC for a neutral then using a rule for a feeder for a branch circuit?
talk about mixing apples and oranges:lol:
Alright, I admit I am toast. I had to throw whatever I could out there.
I am taking my ball and going home.![]()
Sorry I wasn't meaning as bad as I don't think I have an answer either, I'm not up to date on some of these newer changes and barely have been getting the 208 digested which we just changed to. looks like it will be awhile till we are on the 2011.
I do the same thing, through out what I think and hope someone will show me what is correct.
I see the logic but can you cite a code section that makes this a requirement?
To the OP:
Now that this has been discussed some, please tell us your application for this. It might aid in the answer. IE., is the #10 for voltage drop?
I guess I have a question:
If I have a circuit that is just a little over the 5% voltage drop and just up sizing the hot would bring it back down is there a code that would prevent me from only up sizing the hot and not the neutral?